RE: Low Flow Rate Error - 8 kW Ideal Logic ASHP - Help!
By Wh0am3ye, 3 weeks ago |
|
| Thank you for all your responses! I gave the magnetic filter another clean and got the mesh out this time. Flow rate back up to 24.5l/min! Success! I will take a look to see if we have any Y-strainers... | ||
|
|
RE: Low Flow Rate Error - 8 kW Ideal Logic ASHP - Help!
By ASHP-BOBBA, 3 weeks ago |
|
| @editor we now fit 800 micron Y strainers rather than the very standard 100Mic, Samsung and a couple of other makes are very sensitive to low flow and we found when servicing as we don't fit Samsung u... | ||
|
|
RE: Repiping and Reconfiguring our Heat Pump System Including Removing the Buffer Tank - Heat Pump Retrofix
By Mars, 3 weeks ago |
|
| As promised, here's Cap'n Burrows delivering on his promise during a long day of filming. Nearly fours of raw content to edit! Enjoy the short clip. Attachment : Pirate Rich.mp4 | ||
|
|
RE: Low Flow Rate Error - 8 kW Ideal Logic ASHP - Help!
By Mars, 3 weeks ago |
|
| @wh0am3ye, as @ashp-bobba has pointed out, most flow errors on heat pump systems are caused by a blocked Y-strainer. What's remarkable about them is that they don't require a lot of dirt/corrosive bit... | ||
|
|
RE: Heat Pump Installers: Competence, Illusion and the Hard Truth Homeowners Must Face
By Mars, 3 weeks ago |
|
| @Fiona, I really don’t want to disappoint you, but I have to be honest... many homeowners have gone down this route before with MPs and government departments, and unfortunately, we're yet to see a me... | ||
|
|
RE: Are We Sleepwalking Into Another Race to the Bottom?
By Mars, 3 weeks ago |
|
| @dgclimatecontrol, hard to disagree with that. “Zero disrupt” is an impossibility unless you’re happy to accept a system that’s only half-fit for purpose in a lot of UK properties. The industry keeps... | ||
|
|
RE: Are We Sleepwalking Into Another Race to the Bottom?
By Mars, 3 weeks ago |
|
| @shaun, I couldn’t agree more. And thank you for the kind words about the book, really appreciate that, and thanks for your support. I also absolutely love the phrase ZeroDisappointment. You’ve nailed... | ||
|
|
RE: Mixergy Tank Failure
By Mars, 3 weeks ago |
|
| @bontwoody, I completely agree. I have to say, the level of support here has been really disappointing especially from a brand as established and reputable as Mixergy. I genuinely can’t understand why... | ||
|
|
RE: Low Flow Rate Error - 8 kW Ideal Logic ASHP - Help!
By ASHP-BOBBA, 3 weeks ago |
|
| @wh0am3ye Check out by the ASHP on the pipes next to the unit and see if there is a Y strainer this is usually the culprit to look for 1st Attachment : download.jpg | ||
|
|
RE: Daikin 9kW to 8kW Swap Offer from Octopus
By ASHP-BOBBA, 3 weeks ago |
|
| @matban I would have to check the CIBSE guide as we have a software for this but its something like 3x for Kitchen and bathroom 2x for some other areas and 1.5 across the board in other areas but is s... | ||
- 26 Forums
- 2,262 Topics
- 50.5 K Posts
- 704 Online
- 5,922 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Help me keep the faith with my air source heat pump installation
I have only just spotted this post, sorry I missed it e...
By JamesPa , 4 hours ago
-
RE: Oil Boiler & Heat Pump Hybrid System
@paultheheating, where in the country are you?
By Mars , 7 hours ago
-
RE: British Gas Heat Pump Installation Complaint
@bgno, the other consideration for legionella cycles ar...
By Mars , 7 hours ago
-
RE: Electricity price predictions
Remember that almost all submissions to Government Publ...
By Transparent , 10 hours ago
-
@old_scientist I dont monitor the tank temperature but ...
By bontwoody , 11 hours ago
-
RE: Say hello and introduce yourself
Hello @paultheheating - I'm a rural Moderator! What's...
By Transparent , 11 hours ago
-
RE: What valves to replace radbots?
Yes. Radbots just replace TRV heads. TRV heads push t...
By JamesPa , 14 hours ago
-
RE: Who has a V2G EV installation
Im looking at Anderson or Simpson and Partners, somethi...
By AgentGeorge , 16 hours ago
-
RE: When will fusion be producing energy?
I am thinking of the case where AI was able to distingu...
By Batpred , 1 day ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
@majordennisbloodnok Thanks for the welcome and yes I...
By Mark Nelson , 1 day ago
-
RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
I’ve got 5.4kW array, 9.6kWh battery, 5kW heat pump, EV...
By Gruff2001 , 1 day ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
Very definitely. I think the market has changed a bit...
By JamesPa , 1 day ago
-
RE: Buying large amp bidirectional RCD and RCBO
The following diagram is taken from the Meter Operator'...
By Transparent , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@allyfish It was going so well with month after month s...
By Toodles , 2 days ago
-
RE: UFH downstairs and radiators upstairs balancing question
Have you tried turning up the stat and turning down the...
By JamesPa , 2 days ago
-
-
RE: Mediation with RECC, what's your experience?
Welcome to the forums @treewizard and sorry to hear abo...
By Mars , 2 days ago
-
RE: New build installation query
That accounts for why you start with an overly-high DHW...
By Transparent , 2 days ago
-
RE: Daikin Altherma 3 / HomeAssistant
I would have thought that (instantaneous) power is a fa...
By JamesPa , 2 days ago