<?xml version="1.0" encoding="UTF-8"?>        <rss version="2.0"
             xmlns:atom="http://www.w3.org/2005/Atom"
             xmlns:dc="http://purl.org/dc/elements/1.1/"
             xmlns:sy="http://purl.org/rss/1.0/modules/syndication/"
             xmlns:admin="http://webns.net/mvcb/"
             xmlns:rdf="http://www.w3.org/1999/02/22-rdf-syntax-ns#"
             xmlns:content="http://purl.org/rss/1.0/modules/content/">
        <channel>
            <title>
									Increasing Demand on my Electricity Supply - Your Home				            </title>
            <link>https://renewableheatinghub.co.uk/forums/inside-the-home/increasing-demand-on-my-electricity-supply/</link>
            <description>Questions and discussions about renewable heating and heat pumps</description>
            <language>en-GB</language>
            <lastBuildDate>Tue, 21 Apr 2026 16:53:12 +0000</lastBuildDate>
            <generator>wpForo</generator>
            <ttl>60</ttl>
							                    <item>
                        <title>RE: Increasing Demand on my Electricity Supply</title>
                        <link>https://renewableheatinghub.co.uk/forums/inside-the-home/increasing-demand-on-my-electricity-supply/paged/2/#post-43314</link>
                        <pubDate>Sun, 02 Mar 2025 09:44:53 +0000</pubDate>
                        <description><![CDATA[I think there&#039;s a lot of homes where the DNO&#039;s records are incorrect...... and that has a knock-on effect when the householder tries to &#039;do the right thing&#039; and install a heat pump, for exam...]]></description>
                        <content:encoded><![CDATA[<p></p>
<p>One wonders how many installations there are out there that have occurred under various government schemes where the DNO has not been correctly notified. I've spoken with a few people lately who've had solar panels installed and had no idea they may be generating more electricity than they can consume, and can be paid for the exported excess under SEG.</p>
<p></p>
<p>I think there's a lot of homes where the DNO's records are incorrect...<br />... and that has a knock-on effect when the householder tries to 'do the right thing' and install a heat pump, for example.</p>
<p>But those of us in the general public <span style="text-decoration: underline">are</span> in a position where we can do something about it.</p>
<p>DNOs are very happy to receive information from us which adds to their knowledge of the LV network in particular (that's everything below 1000v).</p>
<p> </p>
<p>Personally I'd be much happier to help people install <span style="color: #008000"><strong>storage batteries</strong></span> rather than attempt to earn income from the SEG.</p>
<p>The present system of tariffs and regulatory financial controls are not a good match for the way in which the grid actually works.<br />The costs of operating and maintaining the grid would be lower if the rules reflected 'good science'.</p>
<p>We shouldn't be relying on future income from exporting electricity in our RoI calculations.</p>
<p>That income stream can be swept away by a single change of policy from DESNZ or a Directive issued by Ofgem.</p>
<p>Adding in-house electricity storage</p>
<ul>
<li>reduces grid loading at times of peak demand</li>
<li>reduces losses due to phase imbalance at the local substation</li>
<li>adds resilience for both the household and the grid</li>
</ul>
<p> </p>
<p>@old_scientist and I are each waiting for the other one to start a new Topic which lays out the various different approaches to battery storage.</p>
<p>Any day now, one of us will have enough time to do so.</p>]]></content:encoded>
						                            <category domain="https://renewableheatinghub.co.uk/forums/inside-the-home/">Your Home</category>                        <dc:creator>Transparent</dc:creator>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/inside-the-home/increasing-demand-on-my-electricity-supply/paged/2/#post-43314</guid>
                    </item>
				                    <item>
                        <title>RE: Increasing Demand on my Electricity Supply</title>
                        <link>https://renewableheatinghub.co.uk/forums/inside-the-home/increasing-demand-on-my-electricity-supply/paged/2/#post-43250</link>
                        <pubDate>Fri, 28 Feb 2025 15:56:51 +0000</pubDate>
                        <description><![CDATA[I agree.  I have my own doubts about the veracity of the data @transparent provided for my local substation.  I wonder where we&#039;d be without the level of industry regulation we presently enj...]]></description>
                        <content:encoded><![CDATA[<p></p>
<p>One wonders how many installations there are out there that have occurred under various government schemes where the DNO has not been correctly notified.</p>
<p></p>
<p>I agree.  I have my own doubts about the veracity of the data @transparent provided for my local substation.  I wonder where we'd be without the level of industry regulation we presently enjoy&#x1f631;.</p>]]></content:encoded>
						                            <category domain="https://renewableheatinghub.co.uk/forums/inside-the-home/">Your Home</category>                        <dc:creator>IanMK13</dc:creator>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/inside-the-home/increasing-demand-on-my-electricity-supply/paged/2/#post-43250</guid>
                    </item>
				                    <item>
                        <title>RE: Increasing Demand on my Electricity Supply</title>
                        <link>https://renewableheatinghub.co.uk/forums/inside-the-home/increasing-demand-on-my-electricity-supply/paged/2/#post-43247</link>
                        <pubDate>Fri, 28 Feb 2025 14:33:27 +0000</pubDate>
                        <description><![CDATA[With respect to the original topic in this post, back in the summer I had a 12kW ASHP (permitted development) and 3.645kWp solar array with 3.0kW inverter (G98) installed under the ECO4 sche...]]></description>
                        <content:encoded><![CDATA[<p>With respect to the original topic in this post, back in the summer I had a 12kW ASHP (permitted development) and 3.645kWp solar array with 3.0kW inverter (G98) installed under the ECO4 scheme.</p>
<p>Whilst the general installation was excellent, the paperwork and permissions were a little lacking. After all the works were completed, I chased up my solar installer for he MCS cert and DNO letter to register with my electricity provider for SEG. Eventually I gave up waiting on them and contacted NG directly. NG were brilliant, they informed me they had yet to be notified of the solar install, and advised me I could submit the details myself as I was familiar with the equipment that had been installed. NG issued the letter the next day by email, and I was able to register for SEG.</p>
<p>Next issue was my fuse. I was on a 60A fuse and wanted that upgraded to 80A which I understood NG would do free of charge, so I contacted them about that (as I understand it, the electrician probably should have assessed my demand and had the fuse updated before the installation). It then transpired they had not been notified of the ASHP installation either. Again, NG were extremely helpful in assisting me with the required paperwork, and a few days later an engineer phoned me to arrange a time to upgrade the fuse. He was on site for all of 10mins, electricity off, swapped the fuse, and back on again just in time to make us both a cup of tea. There was some discussion around our maximum demand (as we have 12kW ASHP, 9kW electric shower, 2.7kW+2.5kW double electric oven ...) and could theoretically pull over 80A if everything were on at the same time, but they were happy 80A would be OK. As mentioned previously, NG now have a policy of 80A max, see here:</p>
<p>https://www.nationalgrid.co.uk/downloads-view-reciteme/633928</p>
<p>One wonders how many installations there are out there that have occurred under various government schemes where the DNO has not been correctly notified. I've spoken with a few people lately who've had solar panels installed and had no idea they may be generating more electricity than they can consume, and can be paid for the exported excess under SEG.</p>]]></content:encoded>
						                            <category domain="https://renewableheatinghub.co.uk/forums/inside-the-home/">Your Home</category>                        <dc:creator>Old_Scientist</dc:creator>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/inside-the-home/increasing-demand-on-my-electricity-supply/paged/2/#post-43247</guid>
                    </item>
				                    <item>
                        <title>RE: Increasing Demand on my Electricity Supply</title>
                        <link>https://renewableheatinghub.co.uk/forums/inside-the-home/increasing-demand-on-my-electricity-supply/paged/2/#post-43245</link>
                        <pubDate>Fri, 28 Feb 2025 14:03:37 +0000</pubDate>
                        <description><![CDATA[Thank you!
The solar uptake seems high at 33.3%.
The numbers may well be higher, as I know at least one of my neighbours has battery storage, which obviously has not been notified.]]></description>
                        <content:encoded><![CDATA[
<p></p>
<p>Are you able to share information about our substation</p>
<p></p>
<p>Sure. Here 'tis</p>
<ul>
<li>Transformer size: 315kVA, with four Feeds</li>
<li>Daytime max. demand: 145kVA</li>
<li>Night-time max. demand: 89kVA</li>
<li>Connected properties: 123</li>
<li>EV chargers: 3 (assumed to be 7½kW each)</li>
<li>Heat pumps: 6</li>
<li>Solar generation: 41 properties</li>
<li>Storage batteries: none</li>
</ul>
<p> </p>
<p>Let's remember that these consumer statistics are based on G83/98/99 and LCT applications which are correctly made to NGED.</p>
<p>Where householders or installers have not sought permission, then the data will be incorrect.</p>
<p>Whenever there are obvious anomalies, NGED has a 'sniffer' which can be deployed.<br />That might be used, for example, if underground cables or the transformer itself are getting hot.</p>
<p></p>
<p>Thank you!</p>
<p>The solar uptake seems high at 33.3%.</p>
<p>The numbers may well be higher, as I know at least one of my neighbours has battery storage, which obviously has not been notified.</p>
<p> </p>]]></content:encoded>
						                            <category domain="https://renewableheatinghub.co.uk/forums/inside-the-home/">Your Home</category>                        <dc:creator>Old_Scientist</dc:creator>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/inside-the-home/increasing-demand-on-my-electricity-supply/paged/2/#post-43245</guid>
                    </item>
				                    <item>
                        <title>RE: Increasing Demand on my Electricity Supply</title>
                        <link>https://renewableheatinghub.co.uk/forums/inside-the-home/increasing-demand-on-my-electricity-supply/paged/2/#post-43233</link>
                        <pubDate>Fri, 28 Feb 2025 09:50:48 +0000</pubDate>
                        <description><![CDATA[Sure. Here &#039;tis

Transformer size: 315kVA, with four Feeds
Daytime max. demand: 145kVA
Night-time max. demand: 89kVA
Connected properties: 123
EV chargers: 3 (assumed to be 7½kW each)...]]></description>
                        <content:encoded><![CDATA[<p></p>
<p>Are you able to share information about our substation</p>
<p></p>
<p>Sure. Here 'tis</p>
<ul>
<li>Transformer size: 315kVA, with four Feeds</li>
<li>Daytime max. demand: 145kVA</li>
<li>Night-time max. demand: 89kVA</li>
<li>Connected properties: 123</li>
<li>EV chargers: 3 (assumed to be 7½kW each)</li>
<li>Heat pumps: 6</li>
<li>Solar generation: 41 properties</li>
<li>Storage batteries: none</li>
</ul>
<p> </p>
<p>Let's remember that these consumer statistics are based on G83/98/99 and LCT applications which are correctly made to NGED.</p>
<p>Where householders or installers have not sought permission, then the data will be incorrect.</p>
<p>Whenever there are obvious anomalies, NGED has a 'sniffer' which can be deployed.<br />That might be used, for example, if underground cables or the transformer itself are getting hot.</p>]]></content:encoded>
						                            <category domain="https://renewableheatinghub.co.uk/forums/inside-the-home/">Your Home</category>                        <dc:creator>Transparent</dc:creator>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/inside-the-home/increasing-demand-on-my-electricity-supply/paged/2/#post-43233</guid>
                    </item>
				                    <item>
                        <title>RE: Increasing Demand on my Electricity Supply</title>
                        <link>https://renewableheatinghub.co.uk/forums/inside-the-home/increasing-demand-on-my-electricity-supply/paged/2/#post-43223</link>
                        <pubDate>Fri, 28 Feb 2025 08:31:15 +0000</pubDate>
                        <description><![CDATA[@old_scientist I am similarly frustrated. I am in a different situation in that my property is furthest from my local substation so my inverters will have a lower mains supply voltage to ove...]]></description>
                        <content:encoded><![CDATA[@old_scientist I am similarly frustrated. I am in a different situation in that my property is furthest from my local substation so my inverters will have a lower mains supply voltage to overcome when exporting to my neighbours. However, if the transformer taps in the substation have been configured for a particular load from the houses connected then I can imagine that any reduction in power output from the substation, as a result of me supplying power to my neighbours from the other end of the supply cable, will result in a higher supply voltage for those neighbours nearer the substation due to there being a lower voltage drop from the substation. It’s now easy to see why the difference between day and night load on a substation becomes a problem. Add the need to balance loads on the 3 phases and we can then appreciate the problems the DNO has with the ‘last mile’.]]></content:encoded>
						                            <category domain="https://renewableheatinghub.co.uk/forums/inside-the-home/">Your Home</category>                        <dc:creator>IanMK13</dc:creator>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/inside-the-home/increasing-demand-on-my-electricity-supply/paged/2/#post-43223</guid>
                    </item>
				                    <item>
                        <title>RE: Increasing Demand on my Electricity Supply</title>
                        <link>https://renewableheatinghub.co.uk/forums/inside-the-home/increasing-demand-on-my-electricity-supply/paged/2/#post-43211</link>
                        <pubDate>Fri, 28 Feb 2025 01:06:34 +0000</pubDate>
                        <description><![CDATA[@transparent Thank you for the great explanation, and for the exchanges today - really appreciate your help in gaining a better understanding of the issues involved.
It&#039;s frustrating to wan...]]></description>
                        <content:encoded><![CDATA[<p>@transparent Thank you for the great explanation, and for the exchanges today - really appreciate your help in gaining a better understanding of the issues involved.</p>
<p>It's frustrating to want to be more self sufficient / greener, and to be prevented from doing so. For others benefit, our property is located right next to the substation. The 3 closest properties to the substation (ours included) all had ASHP/solar installs in the summer, and one had a battery install too, although each would have been G98 (3.68kW). I guess part of the problem is we are all exporting at the same time as we all experience the same sunny periods, and if we are all exporting, there is no one to consume it. Am I right to infer from your explanation that properties further away from the substation would not consume our export?</p>
<p>We were hoping to add a further 3.56kWp (giving 7.2kWp total) plus battery storage which would have roughly covered our annual consumption. G99 application is in (courtesy of the installer), but it doesn't sound promising. If they won't grant more than the 3.68kW we already have on G98 (effectively denying the application), it looks like we will be asking for our deposit back. We should know in a few weeks.</p>
<p>@transparent Are you able to share information about our substation (either here or privately), including number of properties connected, and what solar/batteries/ASHPs etc may be installed in the locality?</p>]]></content:encoded>
						                            <category domain="https://renewableheatinghub.co.uk/forums/inside-the-home/">Your Home</category>                        <dc:creator>Old_Scientist</dc:creator>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/inside-the-home/increasing-demand-on-my-electricity-supply/paged/2/#post-43211</guid>
                    </item>
				                    <item>
                        <title>RE: Increasing Demand on my Electricity Supply</title>
                        <link>https://renewableheatinghub.co.uk/forums/inside-the-home/increasing-demand-on-my-electricity-supply/#post-43195</link>
                        <pubDate>Thu, 27 Feb 2025 20:52:07 +0000</pubDate>
                        <description><![CDATA[I&#039;ve been exchanging DMs with @old_scientist during the past day.
In his case the house is very close to the local substation.That means he is unlikely to be permitted to export more than t...]]></description>
                        <content:encoded><![CDATA[<p>I've been exchanging DMs with @old_scientist during the past day.</p>
<p>In his case the house is very close to the local substation.<br />That means he is unlikely to be permitted to export more than the usual 16A (3.68kW).</p>
<p>Being close to your local substation means that there are fewer houses between you and the transformer.<br />Anything you export is less likely to be used <span style="text-decoration: underline">within</span> the area served by that substation,<br />so there's a greater chance of it causing losses at the transformer due to phase-imbalance and harmonics.</p>
<p> </p>
<p>The greater the distance between the house and the substation, the lower will be the mains voltage.</p>
<p>Every cable has a small, but finite, resistance.<br />That creates a voltage drop along the cable length.</p>
<p>To export to the grid, the inverter must raise its output voltage:</p>
10636
<p>The higher the voltage difference between the inverter and the grid, the more current will flow.</p>
<p>However, the maximum voltage must not exceed 253v.<br />That's the statutory limit imposed by <a href="https://www.legislation.gov.uk/uksi/2002/2665/regulation/27" target="_blank" rel="noopener">Section 27 of the The Electricity Safety, Quality and Continuity Regulations</a> (2002).</p>
<p>The G98 certification for devices which can export to the grid enforces this rule.<br />If the grid voltage rises to 253v, then the inverter must cease operating, and effectively detach itself from the grid.</p>
<p> </p>
<p>When applying to the DNO for G99, and requesting export above 16A (per phase),<br />the <span style="text-decoration: underline">further</span> you are from the transformer, the more likely it is that you will be permitted a higher level of export.</p>
<p>A significant proportion of what you export will be taken by houses between you and the substation.</p>]]></content:encoded>
						                            <category domain="https://renewableheatinghub.co.uk/forums/inside-the-home/">Your Home</category>                        <dc:creator>Transparent</dc:creator>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/inside-the-home/increasing-demand-on-my-electricity-supply/#post-43195</guid>
                    </item>
				                    <item>
                        <title>RE: Increasing Demand on my Electricity Supply</title>
                        <link>https://renewableheatinghub.co.uk/forums/inside-the-home/increasing-demand-on-my-electricity-supply/#post-43184</link>
                        <pubDate>Thu, 27 Feb 2025 17:56:38 +0000</pubDate>
                        <description><![CDATA[Yes, that&#039;s what I was thinking.  That would be a shame as I otherwise like the product and the company.  In retrospect, I haven&#039;t found the accompanying App and Portal as essential as I had...]]></description>
                        <content:encoded><![CDATA[<p></p>
<p>If its power rating takes you in the direction of a 3ph supply to the house (using NGED calculations),<br />then it's probably more viable to sell on the GivEnergy unit.</p>
<p></p>
<p>Yes, that's what I was thinking.  That would be a shame as I otherwise like the product and the company.  In retrospect, I haven't found the accompanying App and Portal as essential as I had expected. Control via Home Assistant and 'community-provided automations' has been more than adequate.</p>]]></content:encoded>
						                            <category domain="https://renewableheatinghub.co.uk/forums/inside-the-home/">Your Home</category>                        <dc:creator>IanMK13</dc:creator>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/inside-the-home/increasing-demand-on-my-electricity-supply/#post-43184</guid>
                    </item>
				                    <item>
                        <title>RE: Increasing Demand on my Electricity Supply</title>
                        <link>https://renewableheatinghub.co.uk/forums/inside-the-home/increasing-demand-on-my-electricity-supply/#post-43173</link>
                        <pubDate>Thu, 27 Feb 2025 15:22:40 +0000</pubDate>
                        <description><![CDATA[I don&#039;t know their product history well enough.
I know that the separate inverter and battery combinations used 52v LiFePO4 battery packs.Perhaps all the AIO units were always higher voltag...]]></description>
                        <content:encoded><![CDATA[<p>I don't know their product history well enough.</p>
<p>I know that the <span style="text-decoration: underline">separate</span> inverter and battery combinations used 52v LiFePO4 battery packs.<br />Perhaps all the AIO units were always higher voltage.</p>
<p>GivEnergy <span style="text-decoration: underline">had</span> to change.</p>
<p>Their inverters were only capable of delivering 50% of the rated power when drawing <span style="text-decoration: underline">from</span> the battery,<br />and they couldn't operate in parallel to increase power output.</p>
<p>A new design engineer, Mick, joined them about a year ago.<br />That's what's brought about the radical change.</p>
<p> </p>
<p>Your future direction rather depends on the <span style="color: #008080"><strong>size of heat-pump</strong></span> you're going to need.</p>
<p>If its power rating takes you in the direction of a 3ph supply to the house (using NGED calculations),<br />then it's probably more viable to sell on the GivEnergy unit.</p>
<p>Instead, buy a 3-phase inverter with adequate power to run the house (incl the heat-pump) in an 'off-grid' mode,<br />ensuring that it can be configured for Zero Export, and is approved for that on the ENA database.</p>
<p>Then add as many <a href="https://renewableheatinghub.co.uk/forums/energy-storage/new-fogstar-15-5kwh-upright-solution" target="_blank" rel="noopener">Fogstar self-assembly cabinets</a> as you require.<br />Each will have a capacity of around 14 - 16kWh (depending on your choice of cells), and operate at 52v.</p>
10632]]></content:encoded>
						                            <category domain="https://renewableheatinghub.co.uk/forums/inside-the-home/">Your Home</category>                        <dc:creator>Transparent</dc:creator>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/inside-the-home/increasing-demand-on-my-electricity-supply/#post-43173</guid>
                    </item>
							        </channel>
        </rss>
		