&quot;But we now have devices which draw high current for extensive periods of time, and you&#039;d expect 25mm² wire to be the norm.&quot;
Agreed and my understanding when I changed my CU m...]]></description>
                        <content:encoded><![CDATA[<p>@transparent</p>
<p><span>"But we now have devices which draw high current for extensive periods of time, and you'd expect 25mm² wire to be the norm."</span></p>
<p>Agreed and my understanding when I changed my CU many years ago was that nothing less than 25 mm tails were acceptable then, let alone now, and the DNO cable supply size was up to them, not for us to even know about. Maybe the meter replacement installer knew that as he had arrived with the isolating switch and meter pre-wired to connect to the cut out fused at 100A. I really think we deserve to know more about how our electric supply works and is connected  thank you @transparent .</p>]]></content:encoded>
						                            <category domain="https://renewableheatinghub.co.uk/forums/electric-vehicles-tvs/">Renewable-powered transport (EVs &amp; e-bikes)</category>                        <dc:creator>Jancold</dc:creator>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/electric-vehicles-tvs/can-i-add-an-ev-charger-to-a-full-consumer-unit-by-coupling-with-a-garage-db/#post-44467</guid>
                        <link>https://renewableheatinghub.co.uk/forums/electric-vehicles-tvs/can-i-add-an-ev-charger-to-a-full-consumer-unit-by-coupling-with-a-garage-db/#post-44466</link>
                        <pubDate>Sun, 23 Mar 2025 21:02:34 +0000</pubDate>
                        <description><![CDATA[As I understand it, if a slowly rising common mode DC is passed through the AC only type of RCDs then it will saturate the core in it, and then it can’t detect any signals.  This means that ...]]></description>
                        <content:encoded><![CDATA[<p>As I understand it, if a slowly rising common mode DC is passed through the AC only type of RCDs then it will saturate the core in it, and then it can’t detect any signals.  This means that not only will that dc not trip it, but not will any subsequent ac fault current.  This is especially critical for some fuse boxes which have one RCD covering many MCBs - if any of them have a small dc offset, then none of the circuits will have RCD based protection.  I’m not sure which electronics is most likely to impose dc fault currents though - why are car chargers worse than high power computer power supplies, which have similar high power switch mode systems.  In contrast resistive loads and old fashioned 50Hz transformers won’t have this dc fault current.</p>]]></content:encoded>
						                            <category domain="https://renewableheatinghub.co.uk/forums/electric-vehicles-tvs/">Renewable-powered transport (EVs &amp; e-bikes)</category>                        <dc:creator>robl</dc:creator>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/electric-vehicles-tvs/can-i-add-an-ev-charger-to-a-full-consumer-unit-by-coupling-with-a-garage-db/#post-44466</guid>
                        <link>https://renewableheatinghub.co.uk/forums/electric-vehicles-tvs/can-i-add-an-ev-charger-to-a-full-consumer-unit-by-coupling-with-a-garage-db/#post-44464</link>
                        <pubDate>Sun, 23 Mar 2025 16:56:30 +0000</pubDate>
                        <description><![CDATA[Yes @bontwoody
but it depends what that RCD is.
If it&#039;s just a standard AC-rated unit, then it&#039;s unlikely to be suitable for an EV charger.They&#039;re renowned for imposing DC leakage curre...]]></description>
                        <content:encoded><![CDATA[<p>Yes @bontwoody</p>
<p>but it depends what that RCD is.</p>
<p>If it's just a standard AC-rated unit, then it's unlikely to be suitable for an EV charger.<br />They're renowned for imposing DC leakage currents.</p>]]></content:encoded>
						                            <category domain="https://renewableheatinghub.co.uk/forums/electric-vehicles-tvs/">Renewable-powered transport (EVs &amp; e-bikes)</category>                        <dc:creator>Transparent</dc:creator>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/electric-vehicles-tvs/can-i-add-an-ev-charger-to-a-full-consumer-unit-by-coupling-with-a-garage-db/#post-44464</guid>
                        <link>https://renewableheatinghub.co.uk/forums/electric-vehicles-tvs/can-i-add-an-ev-charger-to-a-full-consumer-unit-by-coupling-with-a-garage-db/#post-44463</link>
                        <pubDate>Sun, 23 Mar 2025 15:43:08 +0000</pubDate>
                        <description><![CDATA[@transparent I had two RCDs in my consumer unit and have just taken out one and replaced the MCBs it was supplying with RCBOs. That created two empty slots. I suppose you could keep the car ...]]></description>
                        <content:encoded><![CDATA[@transparent I had two RCDs in my consumer unit and have just taken out one and replaced the MCBs it was supplying with RCBOs. That created two empty slots. I suppose you could keep the car charger on the remaining RCD and just move some other circuits to the RCBOs]]></content:encoded>
						                            <category domain="https://renewableheatinghub.co.uk/forums/electric-vehicles-tvs/">Renewable-powered transport (EVs &amp; e-bikes)</category>                        <dc:creator>bontwoody</dc:creator>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/electric-vehicles-tvs/can-i-add-an-ev-charger-to-a-full-consumer-unit-by-coupling-with-a-garage-db/#post-44463</guid>
                        <link>https://renewableheatinghub.co.uk/forums/electric-vehicles-tvs/can-i-add-an-ev-charger-to-a-full-consumer-unit-by-coupling-with-a-garage-db/#post-44462</link>
                        <pubDate>Sun, 23 Mar 2025 14:31:24 +0000</pubDate>
                        <description><![CDATA[That depends on whether your EV charger requires Type-A or Type-B  RCD protection.There are no RCBOs with Type-B (DC fault detection).
Type-B RCDs are obviously &#039;better&#039;, but fearfully...]]></description>
<p>Have you considered making space in your consumer unit by using RCBO's instead of RCDs and MCBs?</p>
<p>That depends on whether your EV charger requires Type-A or Type-B  RCD protection.<br />There are no RCBOs with Type-B (DC fault detection).</p>
10973
<p>Type-B RCDs are obviously 'better', but fearfully expensive.</p>
<p>When I bought my Chint NL210-63-463/30 RCD, the list price was above £250 +VAT.</p>
<p>As it's a safety device, the manufacturer and <span style="text-decoration: underline">where</span> you get it from matters.<br />I can import a Chint RCD type-B from the Far East for £50, but the only thing 'Chint' about it is the printing on the front.</p>
<p>I wouldn't trust it to save my life in the event of a fault. &#x1f914; </p>]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/electric-vehicles-tvs/can-i-add-an-ev-charger-to-a-full-consumer-unit-by-coupling-with-a-garage-db/#post-44462</guid>
                        <link>https://renewableheatinghub.co.uk/forums/electric-vehicles-tvs/can-i-add-an-ev-charger-to-a-full-consumer-unit-by-coupling-with-a-garage-db/#post-44461</link>
                        <pubDate>Sun, 23 Mar 2025 14:16:11 +0000</pubDate>
                        <description><![CDATA[It&#039;s quite possible that the incomer to your house is (still) 16mm² of course.
When we had appliances which only switched on periodically, that was regarded as acceptable, and was often con...]]></description>
<p>He also found the Smets 2 smart meter the other installer fitted had 16 mm tails not 25 mm</p>
<p>It's quite possible that the incomer to your house is (still) 16mm² of course.</p>
<p>When we had appliances which only switched on periodically, that was regarded as acceptable, and was often connected to a 100A service fuse.</p>
<p>But we now have devices which draw high current for extensive periods of time, and you'd expect 25mm² wire to be the norm.</p>
<p>Fitting a separate CU for the EV trips is ok, provided it's <strong>clear</strong> whether or not this is energised using the Switch Disconnector on the main CU.</p>
<p>An electrician might decide to use separate Switch Disconnectors, or possibly rely on an isolator on the tails between the meter and the two CUs.</p>
10971
<p>I think it best to <span style="text-decoration: underline">label everything</span> whilst it's still fresh in your mind.</p>
10972]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/electric-vehicles-tvs/can-i-add-an-ev-charger-to-a-full-consumer-unit-by-coupling-with-a-garage-db/#post-44461</guid>
                        <link>https://renewableheatinghub.co.uk/forums/electric-vehicles-tvs/can-i-add-an-ev-charger-to-a-full-consumer-unit-by-coupling-with-a-garage-db/#post-44460</link>
                        <pubDate>Sun, 23 Mar 2025 13:48:05 +0000</pubDate>
                        <description><![CDATA[Since I had dug a trench for the heat pump only for Octopus to say it had sent the wrong diagram, I decided to get Octopus to fix me a Zappi for my EV. I had previously had the House CU repl...]]></description>
                        <content:encoded><![CDATA[<p>Since I had dug a trench for the heat pump only for Octopus to say it had sent the wrong diagram, I decided to get Octopus to fix me a Zappi for my EV. I had previously had the House CU replaced with 5 spare slots for these works and was surprised that the Installer brought a small Proteus CU. He said they always fit their own to avoid responsibility for subsequent faults in the existing house one. Any alterations to a CU renders the electrician responsible for the whole installation. He also found the Smets 2 smart meter the other installer fitted had 16 mm tails not 25 mm , he sorted this out while tidying the board. Next the ASHP people will fit  two more CU's!! The unusual thing I was taught about electrics is that in the event of a serious accident you are guilty until you prove your innocence!!</p>]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/electric-vehicles-tvs/can-i-add-an-ev-charger-to-a-full-consumer-unit-by-coupling-with-a-garage-db/#post-44460</guid>
                        <link>https://renewableheatinghub.co.uk/forums/electric-vehicles-tvs/can-i-add-an-ev-charger-to-a-full-consumer-unit-by-coupling-with-a-garage-db/#post-44459</link>
                        <pubDate>Sun, 23 Mar 2025 12:51:53 +0000</pubDate>
                        <description><![CDATA[Have you considered making space in your consumer unit by using RCBO&#039;s instead of RCDs and MCBs?]]></description>
                        <content:encoded><![CDATA[<p>Have you considered making space in your consumer unit by using RCBO's instead of RCDs and MCBs?</p>]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/electric-vehicles-tvs/can-i-add-an-ev-charger-to-a-full-consumer-unit-by-coupling-with-a-garage-db/#post-44459</guid>
                        <link>https://renewableheatinghub.co.uk/forums/electric-vehicles-tvs/can-i-add-an-ev-charger-to-a-full-consumer-unit-by-coupling-with-a-garage-db/#post-44455</link>
                        <pubDate>Sun, 23 Mar 2025 11:05:01 +0000</pubDate>
                        <description><![CDATA[That&#039;s absolutely the case.
I haven&#039;t (yet) suggested that @editor tells us the cable size/type and distance between the main house CU and the one in the garage.If it were substantial, it m...]]></description>
<p>whether you can add to a garage CU depends on its fuse rating and diversity</p>
<p>That's absolutely the case.</p>
<p>I haven't (yet) suggested that @editor tells us the cable size/type and distance between the main house CU and the one in the garage.<br />If it were substantial, it may indeed offer a route to run an EV charger off the garage unit.</p>
<p>There are formulae for calculating this, which also take into account the ability of that inter-connecting cable to dissipate heat.</p>
<p>Here on the forum I tend to first suggest a strategy which demonstrates best practice,<br />rather than what might 'just about be acceptable' for a particular site.</p>
<p>Yes we have the Wiring Regulations, and the quality of work by the majority of British electricians is very high.</p>
<p>But if we can do better than the basic regulatory requirements, then I think we should do so!</p>
<p>The larger one is fed with 6mm2 cable from its own tiny CU  which is fed from the main tails using henley blocks.  Don’t know why the sparky used Henley’s rather than coming from main CU, there was room. </p>
<p>So we all know - this is a Henley block</p>
10968
<p>It allows three or more cables to be connected together outside of a consumer unit.<br />Most are black, but Proteus offer colour-coded Henleys.</p>
<p>They are too often fitted incorrectly.<br />Typical mistakes are:</p>
<li>Henley block itself not firmly screwed to the backboard</li>
<li>copper conductor gripped by only <span style="text-decoration: underline">one</span> of the internal bolts</li>
<li>the brass bolts not sufficiently tight (creates heat)</li>
<li>the lid-screw not 'sealed' with a wire loop in circumstances when it should be (when it's used with meter tails for example)</li>
<li>the outer insulation of a meter-tail cut back short, which exposes the inner insulation layer</li>
10969
<p>Issues arise when it's <span style="text-decoration: underline">unclear</span> if the Switch Disconnector in the main Consumer Unit will or won't remove power from adjacent Henley Blocks.</p>
<p>I'd need to see a photo of Rob's installation to comment further.</p>]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/electric-vehicles-tvs/can-i-add-an-ev-charger-to-a-full-consumer-unit-by-coupling-with-a-garage-db/#post-44455</guid>
                        <link>https://renewableheatinghub.co.uk/forums/electric-vehicles-tvs/can-i-add-an-ev-charger-to-a-full-consumer-unit-by-coupling-with-a-garage-db/#post-44450</link>
                        <pubDate>Sun, 23 Mar 2025 08:41:58 +0000</pubDate>
                        <description><![CDATA[We have two car chargers with different plugs&#x1f644; - a 32A one and a 10A one.  The larger one is fed with 6mm2 cable from its own tiny CU (looks just like the pic that Transparent posted...]]></description>
                        <content:encoded><![CDATA[<p>We have two car chargers with different plugs&#x1f644; - a 32A one and a 10A one.  The larger one is fed with 6mm2 cable from its own tiny CU (looks just like the pic that Transparent posted) which is fed from the main tails using henley blocks.  Don’t know why the sparky used Henley’s rather than coming from main CU, there was room. </p>
<p>The smaller one is just a leaf granny cable that came with the car, plugs into a socket.  We used to have a ‘proper charger’ for it, and had intended to sell the leaf by now… but Mrs Robl doesn’t like driving the tesla so much these days &#x1f92a;</p>
<p>I expect whether you can add to a garage CU depends on its fuse rating and diversity (is there a home battery charging at night too?)  and what your sparky thinks.</p>]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/electric-vehicles-tvs/can-i-add-an-ev-charger-to-a-full-consumer-unit-by-coupling-with-a-garage-db/#post-44450</guid>