ASHP added to Biomass System?

9 Posts
5 Users
8 Reactions
107 Views
(@vinceprince)
Active Member Member
58 kWhs
Joined: 4 weeks ago
Posts: 6
Topic starter  

We have a biomass system which works fine. Looking at possibilities to improve efficiency and reduce costs. Limited usable roof space for solar.

Would an ASHP work well with the boiler as back up? We have a 1500l buffer tank.

House is victorian stone built in SE Scotland and as well insulated as we can make it!

Thoughts?


   
👍
1
Quote
Mars
 Mars
(@editor)
Illustrious Member Admin
20614 kWhs
Veteran
Joined: 4 years ago
Posts: 2609
 

Welcome to the forums! In quick reply, yes, a biomass boiler can work as a backup. For reference, we have an oil boiler as part of our ASHP system, and it’s configured to assist during defrost cycles and when temperatures drop below -1°C (which isn’t very often). In those instances, the heating switches over to oil as the ASHP becomes less efficient.

One point to consider is the buffer tank – 1,500 litres is quite large. I’m not entirely sure how that impacts efficiency or whether it would need to be bypassed in a bivalent setup. I’ll reach out to some installers I know for further insights and advice.

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Follow our sustainability journey at My Home Farm:https://kirstenandmars.com


   
ReplyQuote
(@derek-m)
Illustrious Member Member
15282 kWhs
Veteran Expert
Joined: 4 years ago
Posts: 4433
 

Posted by: @vinceprince

We have a biomass system which works fine. Looking at possibilities to improve efficiency and reduce costs. Limited usable roof space for solar.

Would an ASHP work well with the boiler as back up? We have a 1500l buffer tank.

House is victorian stone built in SE Scotland and as well insulated as we can make it!

Thoughts?

Rather than being a buffer tank, the 1500l vessel would more likely be a thermal store. Do you now if it contains a heating coil? What is the make and model?

 


   
👍
1
ReplyQuote



Mars
 Mars
(@editor)
Illustrious Member Admin
20614 kWhs
Veteran
Joined: 4 years ago
Posts: 2609
 

@derek-m good point. 

Maybe some of photos of the plant room would be helpful, @vinceprince 

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Follow our sustainability journey at My Home Farm:https://kirstenandmars.com


   
ReplyQuote
(@vinceprince)
Active Member Member
58 kWhs
Joined: 4 weeks ago
Posts: 6
Topic starter  

I'll get some pics when I am back. It has input from the boiler and output for the heating and hor water circuits, but the boiler initially bypasses the tank if heating system is cold and then heats the tank when heat circuit reaches temperature. Heating will run off the tank when boiler reaches set temperature and shuts off.


   
👍
2
ReplyQuote
Sune
 Sune
(@sune)
Trusted Member Contributor
208 kWhs
Expert
Joined: 2 years ago
Posts: 17
 

@vinceprince our company supplies heat pumps, and have been doing biomass systems for much much longer. What you're describing is called a hybrid or bivalent system and is totally doable. However there are some design considerations that it's important to be aware of to keep the running costs of your heat pump low, and to make sure your biomass boiler isn't constantly cycling on and off. 

There are several ways to do it - you can have an either/or system, or one where one tops the other up. You will then have different logic as to when to use each. For example outside temperature may well be a factor. 

I'm happy to help with some possible schematics but would need details of the system (thermal store, type of hot water provision, heat emitter details (rads/underfloor, etc)), as well as what you're hoping to achieve from it. My email is sune@firepower.co.uk  

 

Sustainable Groups - Renewable Heating - Local Government - Director of Firepower


   
👍
1
ReplyQuote
(@johnmo)
Prominent Member Member
2117 kWhs
Joined: 2 years ago
Posts: 407
 

My view

Make sure you heating system can run at a low temp, ideally the lower the better.

Get a separate DHW heat pump suitable unvented cylinder, run this in the normal manner via diverter valve from the ASHP. This allows the big buffer to heated to a temperature more suited to a good CoP from the heat pump and dedicate this to heating only.

Once temperature gets in the sub zero range fire up the biomass.

Another option is keep the cold water feed to buffer coil, and use this as preheated water to an unvented cylinder. This would make reheats quite easy.

Then look around for a heat pump at a bargain price as size is quite flexible.

Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.


   
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
20614 kWhs
Veteran
Joined: 4 years ago
Posts: 2609
 

@vinceprince you'd be well advised to discuss this with @sune. He's one of the best out there.

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Follow our sustainability journey at My Home Farm:https://kirstenandmars.com


   
👍
2
ReplyQuote
(@vinceprince)
Active Member Member
58 kWhs
Joined: 4 weeks ago
Posts: 6
Topic starter  
20240912 181807
20240912 181740

Took some pics, a bit crowded in there at the moment!


   
👍